(/etc/nut/ups.conf
is generated correctly from below file)
/etc/config/nut_server
config driver 'UPS'
option driver usbhid-ups
option port auto
option vendorid 012c
list override 'battery_charge_low'
list override 'battery_runtime_low'
config override 'override_battery_charge_low'
option value '95'
config override 'override_battery_runtime_low'
option value '5000'
config user
option username upsuser
option password upspassword
option upsmon master
config listen_address
option address 0.0.0.0
option port 3493
config upsd 'upsd'
option statepath /var/run/nut
option maxconn 1024
option runas nut
(/etc/nut/upsmon.conf
below as you can see is generated wrongly) There are lines in the generated file that are not in /etc/config/nut_monitor
/etc/config/nut_monitor
config upsmon 'UPS'
option notifycmd '/usr/bin/nut-sendmail-notify'
list defaultnotify 'EXEC'
list defaultnotify 'SYSLOG'
option shutdowncmd /sbin/halt
option deadtime 15
option powerdownflags /var/run/killpower
option onlinemsg "UPS Online"
option onbattmsg "UPS Power is off"
option lowbattmsg "UPS battery low"
option fsdmsg "Router Fsd"
option comokmsg "Router restored Communications with UPS"
option combadmsg "Router lost Communications with UPS"
option shutdowmsg "Router shutting down now"
option replbattmsg "UPS battery needs changing"
config master
option upsname 'UPS'
option hostname 'localhost'
option username 'upsuser'
option password 'upspassword'
option powervalue '1'
/etc/nut/upsmon.conf
RUN_AS_USER nutmon
MINSUPPLIES 1
SHUTDOWNCMD "/sbin/halt"
NOTIFYCMD "/usr/bin/nut-sendmail-notify"
POLLFREQ 5
POLLFREQALERT 5
HOSTSYNC 15
DEADTIME 15
POWERDOWNFLAG /var/run/killpower
NOTIFYMSG ONLINE "UPS Online"
NOTIFYMSG ONBATT "UPS Power is off"
NOTIFYMSG LOWBATT "UPS battery low"
NOTIFYMSG FSD "Router Fsd"
NOTIFYMSG REPLBATT "UPS battery needs changing"
NOTIFYFLAG ONLINE EXEC+SYSLOG
NOTIFYFLAG ONBATT EXEC+SYSLOG
NOTIFYFLAG LOWBATT EXEC+SYSLOG
NOTIFYFLAG FSD EXEC+SYSLOG
NOTIFYFLAG COMMOK EXEC+SYSLOG
NOTIFYFLAG COMMBAD EXEC+SYSLOG
NOTIFYFLAG SHUTDOWN EXEC+SYSLOG
NOTIFYFLAG REPLBATT EXEC+SYSLOG
NOTIFYFLAG NOCOMM EXEC+SYSLOG
NOTIFYFLAG NOPARENT EXEC+SYSLOG
RBWARNTIME 43200
NOCOMMWARNTIME 300
FINALDELAY 5
CERTVERIFY 0
FORCESSL 0
MONITOR UPS@localhost 1 upsuser upspassword master
I set the override_battery_charge_low
& override_battery_runtime_low
to extreme high values to test if the router proceeds with /usr/sbin/halt and killpower to the UPS.
However when attempting to do that, the values of battery_charge_low
& battery_runtime_low
get reached but does not trigger low battery or shutdown. As you can see below when executing upsc UPS
when on battery, it still says ups.status: OB DISCHRG
instead of ups.status: OB LB
. Can anyone tell me why this happens?
battery.charge: 77
battery.charge.low: 95
battery.charge.warning: 50
battery.date: 2001/09/25
battery.mfr.date: 2015/01/10
battery.runtime: 4781
battery.runtime.low: 5000
battery.type: PbAc
battery.voltage: 25.2
battery.voltage.nominal: 24.0
device.mfr: American Power Conversion
device.model: Back-UPS RS 1200G
device.serial: 7C1161V23098
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.synchronous: no
driver.parameter.vendorid: 012c
driver.version: 2.7.4
driver.version.data: APC HID 0.96
driver.version.internal: 0.41
input.sensitivity: medium
input.transfer.high: 294
input.transfer.low: 176
input.transfer.reason: input voltage out of range
input.voltage: 0.0
input.voltage.nominal: 230
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.firmware: 322.L1 .I
ups.firmware.aux: L1
ups.load: 6
ups.mfr: American Power Conversion
ups.mfr.date: 2015/01/10
ups.model: Back-UPS RS 1200G
ups.productid: 0002
ups.realpower.nominal: 720
ups.serial: 7C1161V23098
ups.status: OB DISCHRG
ups.test.result: No test initiated
ups.timer.reboot: 0
ups.timer.shutdown: -1
ups.vendorid: 012c
Im not sure if this has anything to do with /etc/nut/upsmon.conf
being incorrectly generated?
Also one more thing.
Even though my setup is in netserver mode and the UPS is reporting correctly, when doing upsdrvctl start
, i get:
Network UPS Tools - UPS driver controller 2.7.4
Network UPS Tools - Generic HID driver 0.41 (2.7.4)
USB communication driver 0.33
Can't claim USB device [012c:0002]: No such file or directory
Driver failed to start (exit status=1)
Does this matter?
OpenWRT 19.07.7
WRT1200ac
Would appreciate your helps. thanks